Smallest MV Cable Size?

Status
Not open for further replies.

FaradayFF

Senior Member
Location
California
Hi folks,

I need to run #10 Medium voltage cable from overhead line down to a padmount transformer. Can anyone recommend a vendor?
I'm imagining I should have a shielded MV cable for this.

Thanks,
EE
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
The voltage sort of matters.
I've smallest seen are:
3C-#8 5kv
1C - #2, 15kv


Anything above 2.4kv will be shielded.

Most I have dealt with are Okonite. But I don't have a vendor I could recommend.

(edit to add) 310.10.E
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Wow, #10... where you going to find it or a terminator for it?
what voltages do you have there?
 

Todd0x1

Senior Member
Location
CA
#6 5kv mv-105 is only $2something a foot maybe even if you only need #10 per your amperage you will likely end up using something larger
 
Status
Not open for further replies.
Top