Yes, a smoke detector is an "outlet" as defined in Article 100 of the NEC.
Chris
I need to learn to type faster.
Chris
Yes they are. More to the point, a permanently mounted and AC powered smoke detector counts as an "outlet." Any outlet in a dwelling unit bedroom (and in other rooms, if the 2008 NEC is in effect in your area) must be powered be a circuit that has AFCI protection for the entire circuit.
Any outlet in a dwelling unit bedroom (and in other rooms, if the 2008 NEC is in effect in your area) must be powered be a circuit that has AFCI protection for the entire circuit.
...unless of course your in NJ ~ then it is "optional" under the '05 [NJ hasn't accepted the '08 yet]
Does NJ have an exception for 05'? We are on the 05' here and we got to afci the smokes.
NEMA - Code Alert: New Jersey, 07 Nov 20053. Chapter 2 of the electrical subcode, entitled "Wiring and Protection," is amended as follows:
i. Section 210.12(B) of Article 210, entitled "Branch Circuits," is amended to insert the following sentence at the end of the section, "This requirement shall be considered optional."
Not "any outlet" in a bedroom. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets. :wink:
The CMP clearly intended the smoke detectors to be on an AFCI.
We need to protect the wiring to the smokes. Its the same as any other wiring. Plus smokes have battery backup.
Effective Dec 31, 2008 in washington state they may be on an AFCI but not required to.
YES THERE are a lot of beds and furniture pushed up against the smoke detectors this makes perfect sence in an asylum.
AFCIs are required to protect the entire branch circuit, not just the wiring beyond the outlet.
And your point is.......??
AFCIs are required to protect the entire branch circuit, not just the wiring beyond the outlet.