I am wiring a home that will have a mother in law apartment in part of the basement. At some point it may be a rental. Home owner wants a separate meter and wants just standard smoke and carbon detectors- line voltage. I would want the apartment and the house to be tied together but I am not sure that would be compliant. I am assuming I cannot have a branch circuit from the home be connected to a device in the apartment since they are separate meters. Any thoughts.
I assume that I don't have to tie them together but I would surely want it in my home. Is the only way to do this thru a LV system?
They must be wired together if this is considered a single family:
Now this is Ohio's code but it is ICC based.
314.3 Location. Smoke alarms shall be installed in the following locations:
1. In each sleeping room.
2. Outside each separate sleeping area in the immediate vicinity of the
sleeping rooms. Note (by me): the use of sleeping area and sleeping rooms.
3. On each additional story of the dwelling, including basements and
habitable attics but not including crawl spaces and uninhabitable attics. In
dwellings or dwelling units with split levels and without an intervening
door between the adjacent levels, a smoke alarm installed on the upper
level shall suffice for the adjacent lower level provided that the lower level
is less than one full story below the upper level.
When more than one smoke alarm is required to be installed within an individual
dwelling unit the alarm devices shall be interconnected in such a manner that the
actuation of one alarm will activate all of the alarms in the individual unit.