When I look for a bad neutral problem the first thing I do is to check if there is a GEC bond to a city water pipe that can mask a weak or faulty neutral, also cable and shielded phone drops can also add to masking a bad neutral as they are bonded at both the pole and the house, after turning of the main, I lift these connections and make sure that no one is in a proximity of an electrical appliance and a Earth reference point as the grounding can become energized above earth if there is a bad neutral and you load down one leg of the service as there will be no return path back to the source, after lifting the above points, I turn off all the breakers in the panel and any sub-panels, I turn on only the breakers on one leg of the service or I use a separate load such as was mentioned a space heater of at least 1500 watts, then and only then I take my voltage readings being careful to not make a path from anything bonded to the service neutral and earth or other grounding, if I get more then a 10% voltage drop, or even a difference of 100% between the legs of the service, I check to see if it is also at the meter, then I call the POCO and set up a time to be there so I can also lift the masking return paths I mentioned above so that their beast can do its job without the cable, phone shield or water ground or any other return paths that could be masking the bad neutral.
Yes it's a few more steps but that's what we are paid for and we should understand how to safely load only one side of the service after lifting any possible masking return paths that could otherwise let a lost neutral go unfound.
Keep in mind that a RG6 or RG11 cable drop can handle quite a bit of current before you will see a voltage drop, I have seen RG6 catch fire because of a bad neutral, but that was on a very overloaded 120 volt only service that the POCO had already tested with the beast and said it was a good neutral, I wasn't involved and the previous electrician didn't know to lift the cable drop bond at the service before loading the service down with a 100 amp load bank, luckily he put out the burning cable but the homeowner freaked out on him and I was called in.
Just remember that if the neutral connection is lost that doing the above will also bring all grounding of this house or building up to 120 volts to earth, so I can't say enough how much care you must take to make sure no one is in harms way when doing these kinds of test.
Thanks for your post, all excellent points! Obviously my mind shuts off after midnight:ashamed1:
I should have mentioned the best place to do it is at the meter socket with the meter pulled. To be honest, now that I think about it don't do it at the main panel at all, especially if the house has metal water pipes or a gas line. Even if the water bond is disconnected along with the grounding electrode that has the cable/phone bond there is still the furnace with its gas line and an egc running to it. Same thing could be said about a gas range with a 120 volt circuit or an electric water heater. If one was to load bank at the panel current will end up returning from the circuit leading to furnace through the cable's EGC, through the frame and over through the gas line. Same with the water heater. The #10 egc in the romex will carry power from the main panel through the water heater tank to the pipes and out the water main. The 60 amps of stray current may not hurt the gas pipes or water lines, but a #12 EGC in romex stapled across wooden floor joists would get real hot real fast. And truth is if enough parallel EGCs are present say a #12 to a dishwasher with a copper water line with a grounded water valve bracket, a #10 to a water heater with metal piping, a #14 to a gas stove, the furnace gas line, ect ect enough parallel egc paths would be present through the gas and water pipes it would mask and real results from the test.
Any way, reading what I just wrote on my prior post...:jawdrop: Apparently I need to stop posting so late, even Im frightened by what I wrote:happysad:
To the OP, don't do what a previously mentioned at the main panel, and even the meter socket requires caution. I left out a lot on how to do it right:slaphead: