I kept reading through all the posts and was thinking about line length and size never being mentioned, sure sounds to me like voltage drop could be an issue, and is something I have encountered before making someone think they had a neutral problem.Don't forget that a neutral voltage shift of the same size as the voltage drop in the ungrounded conductor is perfectly normal and not a sign of a high resistance neutral.
It is only if the neutral shift is higher than the drop in the ungrounded conductor for a single sided load or if both are excessive that you need to look at drop or transformer neutral issues rather than just overall sizing issues.
In fact in a circuit where a reduced neutral is allowed, you would expect the neutral voltage shift to be higher than the hot lead drop when an unbalanced test load is applied.
Tapatalk!
Not certain if it has been mentioned because I did not read all the posts... but I believe a common cause of furnace board failure is power line surge.
Just a reference to the stereotype that their troubleshooting skills are limited to board replacement rather than root cause analysis.
Tapatalk!
The blunt truth is the electronics in a lot of appliances are complete garbage. They fail ALL the time even under none abusive conditions. Ive lived in many different houses, and over the years almost everything with electronics eventually loses a control board at some time. Some things like microwave ovens I have had luck with, but Ive had dishwashers, ovens, water softeners that would eat control boards even under warrantee. Techs have openly admitted electronic burn outs are common for certain brands or models.
Just recently I lost a control board on a direct vent heater still under warentee:roll:
nothing you buy today is the quality of 20 years ago:rant:
The blunt truth is the electronics in a lot of appliances are complete garbage. They fail ALL the time even under none abusive conditions. Ive lived in many different houses, and over the years almost everything with electronics eventually loses a control board at some time. Some things like microwave ovens I have had luck with, but Ive had dishwashers, ovens, water softeners that would eat control boards even under warrantee. Techs have openly admitted electronic burn outs are common for certain brands or models.
109 volts doesn't sound that low to me.
2 boards go bad. One cause is that they replaced with a defective board (no quality control) or there really is a problem with the furnace and the guy isn't smart enough to trouble-shoot.
If two guys say there isn't a ground and you know there is one that should tell you something. Sounds like standard BS when they don't know.
He pulls the meter and puts this cheesy thing called a 'Super Beast' on the tabs, turns it on and by looking at two crude analog meters.
Why would anyone use such a crude instrument for troubleshooting professionally? It looked like it was made from drain pipe and Radio Shack parts.
There is really nothing wrong with an analog meter for residential trouble-shooting.
A digital meter may impress the customers but an analog will give an accurate reading. They probably used pretty high quality meters for the beast.
There is really nothing wrong with an analog meter for residential trouble-shooting.
A digital meter may impress the customers but an analog will give an accurate reading. They probably used pretty high quality meters for the beast.
My problem was the 0-150 range with 5 volt increments. The increments were about a millimeter apart. A variation of 4 volts would have been almost undetectable. The needle is about a volt wide. Also, moving it around made the needles move. You could get a 5 volt spike just by bumping it.
They accuracy may be the same, but the precision is not.
But the quality of an analog meter (as measured by damage resistance, accuracy and repeatability, for example) does not guarantee that other aspects of the design (such as precision and readability) are in the range needed for examining voltage differences in the several percent range.
Interesting discussion....right down my alley. As a former (now retired) meter/relay tech for the local POCO, I did this kind of diagnosis all the time. The newer Mega-Beast uses digital meters and adds up to 80A load on either side of the service, which locates most service problems pretty well. If the neutral is the only problem, then under load one side will go down and the opposite (unloaded) side will go up by a similar amount. Nearly every service side voltage problem is caused by too long of secondary runs for the service drop size, or an overloaded transformer. Many times the problem was not obvious when I got there because on transformers that are shared by several services, the max load doesn't show up until 5 or 6 PM, (after we've gotten off work) when everyone is home from work cooking, using hot water, kicking on the furnace, etc. The giveaway of service line drop or connection problems is when the loaded voltage readings at the transformer are much better than at the meter. A common connection problem comes when "insulink" crimp style connectors are used on the service conductors. They have a bad habit of filling with water over time, causing corrosion of the aluminum conductors that is not visible from the outside. We quit using 'em years ago and went to "one-bolt or two-bolt" connectors. One problem a lot of customers had with the POCO is that we weren't allowed to diagnose problems beyond the service point. They figured while we were there, we should rip into their sub-panels, water bonds, etc. Big no-no both from a liability standpoint and from local electricians who feel that we were taking their work (and I agree with them). The lineman did all he could without engineering approval of bigger wire or a bigger (or additional transformer to divide the load) and the associated costs. One other thing worth mentioning is that a service neutral or connection problem would likely cause other equipment damage as well. No mention of any blown fuses, burned out bulbs, flickering lights, half of the lights in the house going brighter when the other half go dim?
Just curious.
Interesting discussion....right down my alley. As a former (now retired) meter/relay tech for the local POCO, I did this kind of diagnosis all the time. The newer Mega-Beast uses digital meters and adds up to 80A load on either side of the service, which locates most service problems pretty well. If the neutral is the only problem, then under load one side will go down and the opposite (unloaded) side will go up by a similar amount. Nearly every service side voltage problem is caused by too long of secondary runs for the service drop size, or an overloaded transformer. Many times the problem was not obvious when I got there because on transformers that are shared by several services, the max load doesn't show up until 5 or 6 PM, (after we've gotten off work) when everyone is home from work cooking, using hot water, kicking on the furnace, etc. The giveaway of service line drop or connection problems is when the loaded voltage readings at the transformer are much better than at the meter. A common connection problem comes when "insulink" crimp style connectors are used on the service conductors. They have a bad habit of filling with water over time, causing corrosion of the aluminum conductors that is not visible from the outside. We quit using 'em years ago and went to "one-bolt or two-bolt" connectors. One problem a lot of customers had with the POCO is that we weren't allowed to diagnose problems beyond the service point. They figured while we were there, we should rip into their sub-panels, water bonds, etc. Big no-no both from a liability standpoint and from local electricians who feel that we were taking their work (and I agree with them). The lineman did all he could without engineering approval of bigger wire or a bigger (or additional transformer to divide the load) and the associated costs. One other thing worth mentioning is that a service neutral or connection problem would likely cause other equipment damage as well. No mention of any blown fuses, burned out bulbs, flickering lights, half of the lights in the house going brighter when the other half go dim?
Just curious.
Uness its a full blown open neutral I don't find poor neutrals tripping breakers. Of course when they do the load tends to be burning up at that point.
But like the OP mentioned, 10kva is feeding multiple houses. 10kva is small even for some single houses now a days.
There is really nothing wrong with an analog meter for residential trouble-shooting.
A digital meter may impress the customers but an analog will give an accurate reading. They probably used pretty high quality meters for the beast.
Am I wrong in looking at it like the transformer has about the same capacity as a 10kW portable generator?
Or am I missing something?
The only thing you are missing, IMHO, is that the generator has a hard limit on the power it can deliver longer than instantaneously, based on the engine power.
A transformer on the other hand can deliver almost unlimited overloads until the primary protection trips (if ever) or the temperature rises too high over a period of hours or more.
But during that time the voltage regulation will suffer. The neutral offset will only be that caused by the service wiring.
Tapatalk!