I would bet a milkshake no inverter manufacturer supports connecting an inverter across an open phase B-C of a open delta.
I think the inverter is measuring grid impedance (%Z) of the primary voltage source thru a secondary coil impedance.
Where the open phase (B-C) is likely two unequal transformers in series I think the inverter would get confused, or need to be specially designed for that scenario. I'd like to be wrong about it though.
Since there is no standard or NEC requirement for identifying the open set, like saying A= black , B = orange, C = blue and then require orange / blue (or B-C) is always the open set (if its an open delta), it seems difficult to even tell which set is the open phase.