I have a lot of experience in the industrial industry and not so much in the residential industry. Looking at solar for my house, and the company I'm dealing with seems to be going through a lot of steps that I'm not sure about. I thought it would be as easy as installing a new 240/60A breaker in my panel (SquareD, Homeline, 225A bus, with 200A main breaker).
The company is telling me that due to my transfer switch, that they want to tie-in with splicing bugs on the line side of the 240V/200A main disconnect of the house. I'm not a fan of these, would much rather buy additional lug kit from SquareD (but they are not allowed/permitted on the line side of the disconnect). I proposed having the company tie in to the load side of the disconnect but they claimed it would violate the 120% rule and needed to be on the line side.
The company is telling me that due to my transfer switch, that they want to tie-in with splicing bugs on the line side of the 240V/200A main disconnect of the house. I'm not a fan of these, would much rather buy additional lug kit from SquareD (but they are not allowed/permitted on the line side of the disconnect). I proposed having the company tie in to the load side of the disconnect but they claimed it would violate the 120% rule and needed to be on the line side.