Dang, I didnt realize the complications with this configuration. Definitely making sure its a delta on the utility side next time.
The problem is I have 9 sites with these transformers. 4 of the sites will have a single pole 277V lighting circuit and a 2 pole 480V comm circuit which I will use phase a, b, and c for (I think is best for good balance for nuetral current in this sitiation, correct?). The other 5 sites will only have the 3 phase solar on the 480V side.
All sites have the 208V nuetral bonded to ground at the service. The problem I am seeing with connecting the nuetral to the XO and removing the XO bonding strap, and having the EGC on both the 480V side and 208V (Service) side bonded, is that they are bonded at the service and therefore means the HO neutral is connected to that same path. Am I thinking about that right? Not sure that is preferable.
Therefore I am back to leaving the nuetral conductor off on the XO terminal of the transformer. These are all customer owned transformers and are on the load side of the service (although some are line side taps with a fused disco). All the services are 208/120V wye.
The transformer manufacturer recommended leaving the nuetral XO (on the utility side) disconnected.
Any last thoughts?:/