Can the line side of a feeder be tapped for the solar disconnect as opposed to the line side of the service? The service is at a pedestal 100 yds. away.
The line side of the service disco is 100yds away After that a feeder goes to the panel inside the house. I'm thinking that if that feeder is tapped before the panel in the house that it is non compliant according to 705.12 because it is not upstream of the main breaker 100yds away.Yes, but unless you're connecting to the line side of the service disconnect, you must comply with the restrictions outlined in 705.12(D).
I should have said that there is a 200a disco, and the solar disconnect is 60a, which isn't allowed unless it is tapped on the service side of the main.It could be compliant, as long as it meets the requirements of 705.12(D). It does not meet 705.12(A).
With a 200A main in a panel with a 225A bus (not uncommon) you could have up to a 75A PV backfeed and not need to use a supply side tap.I should have said that there is a 200a disco, and the solar disconnect is 60a, which isn't allowed unless it is tapped on the service side of the main.
Right. The bus may be 225 but no manufacture will tell you that it is unless it is noted on the enclosure somewhere.With a 200A main in a panel with a 225A bus (not uncommon) you could have up to a 75A PV backfeed and not need to use a supply side tap.
Can you cite a code section for that? Unlike the bus, the service wire will never carry the sum of main plus backfeed.The feeder from the service disconnect to the panel would have to be rated for 225A also (actually, minimum 217A) for it to be compliant.
Good point. I guess I was thinking that if OCPD only existed at that 60A and 200A CB's, then the combination feeder/panel bus would be considered all the same node. But you're right -- power from the 200A service disconnect will only flow in that direction, so the node point is really just the panel busbar.Can you cite a code section for that? Unlike the bus, the service wire will never carry the sum of main plus backfeed.
Yep, and many inspectors interpret that part of 705 to apply to feeder wires even when all there is involved is the backfed breaker on one end and the PV on the other. No loads at either end, let alone in the middle of the feeder.For the record, I was looking at a reading of the 2011 705.12(D)(2) -- got tripped up where it said "busbar OR conductor".