Solid wire and crimping

Status
Not open for further replies.

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Can solid wire (say #6 solid) be butt spliced using a crimped connection? I have never seen a solid wire crimped.

Thank you.
 
Can solid wire (say #6 solid) be butt spliced using a crimped connection? I have never seen a solid wire crimped.

Thank you.

Some but by no means all butt splice connectors are rated for solid wire. I would expect to have to use a cycle controlled crimper to match the connectors. No universal crimp pliers if using solid wire.
JMO
 
It is for GEC extension.

The plumbers did a plumbing upgrade and the city has required a new grounding system. The plumbers did not do the GEC properly so the customer wants me to use a butt splice to extend the GEC to the panel and I refused to use a crimp and butt splice on the solid wire.

I said I will replace the whole system properly without a butt splice.
 
It is for GEC extension.

The plumbers did a plumbing upgrade and the city has required a new grounding system. The plumbers did not do the GEC properly so the customer wants me to use a butt splice to extend the GEC to the panel and I refused to use a crimp and butt splice on the solid wire.

I said I will replace the whole system properly without a butt splice.
Cadweld or similar should be adequate but may be more expensive than the new 6.
 
It is for GEC extension.

The plumbers did a plumbing upgrade and the city has required a new grounding system. The plumbers did not do the GEC properly so the customer wants me to use a butt splice to extend the GEC to the panel and I refused to use a crimp and butt splice on the solid wire.

I said I will replace the whole system properly without a butt splice.
Irreversible crimp is all you need.
 
Don't call me stupid, but I've wondered about using a swaging tool and aluminum crimp sleeves. The kind you would use for wire rope or Airline cable.

Never done it, but I thought about it in the past
 
Don't call me stupid, but I've wondered about using a swaging tool and aluminum crimp sleeves. The kind you would use for wire rope or Airline cable.

Never done it, but I thought about it in the past

Funny you mention that. Last spring, I had to extend a Ufer connection to feed a new panel location. #4 wire fits a 3/16" oval copper Nicopress sleeve. Perfectly. Not a listed splice, but DEFINITELY irreversible and low resistance.

IMG_2550.jpg

I did this at my parents' house; I sleep just fine knowing how I did this splice. :)


SceneryDriver
 
Funny you mention that. Last spring, I had to extend a Ufer connection to feed a new panel location. #4 wire fits a 3/16" oval copper Nicopress sleeve. Perfectly. Not a listed splice, but DEFINITELY irreversible and low resistance.

I did this at my parents' house; I sleep just fine knowing how I did this splice. :)


SceneryDriver

heck yeah, I'd sleep okay with that
 
Can solid wire (say #6 solid) be butt spliced using a crimped connection? I have never seen a solid wire crimped.

T&B makes a line of C-Taps that are listed as Grounding and Bonding Equipment (suitable for splicing the GEC) that can be applied by T&B lever action crimpers. The T&B C-Tap #54720 will do two #6 solid copper conductors side-by-side. The #54720 is color coded "brown". The installation instructions are available Here.

I picked up the tool, used, on eBay.
 
I know about the irreversable crimp option offered by NEC. But are the splices listed for SOLID conductor?

ETA: just checked their site. Burndy YC4C6 are good for solid as well.
 
I did this at my parents' house; I sleep just fine knowing how I did this splice. :)


SceneryDriver
care to explain
whatthe.jpg
 
Can solid wire (say #6 solid) be butt spliced using a crimped connection? I have never seen a solid wire crimped.

Thank you.
Copper is malleable so I guess it can be crimped. Even at #6AWG or around 16mm2 would be closest for us in the SI world........:p
Not something I've tried...........
 
I thought that looked funny but didn't blow it up to look at it further. I figured he HAD to have known about it, and didn't share, so it must have been a non-issue. But, well, it sure LOOKS LIKE an issue!
 
Looks like a metal raceway enclosing an GEC that was not properly bonded to it at either end. Perhaps a shot of lightning at some time or another, proving a picture is worth a thousand words.

Personally, I would not bother with putting that type of splice in a box nor would it V.
 