brian john
Senior Member
- Location
- Leesburg, VA
I have looked at literally 100's of projects for harmonic issues and .
Now it may be the area I do most of my work in but the average service and downstream transformers are typically 30%-40% loaded so neutral issues is not a problem.
The few cases where an overload neutral was an issue was on the secondary of a 208/120 Wye transformer that was at 90%-100% load.
We did have issues in the early days of UPS where there were mechanical governors, and no input filters on the UPS.
Additionally when VFD's were replacing motor starters years ago on large projects that had single transformers dedicated to mechanical loads, there were issues with the utility transformers and early generation electronic relaying.
But most harmonic issues I see are not harmonics but typically hardware issues, grounding issues, such as neutrals grounded downstream of the transformer compounded by other wiring issues.
Now it may be the area I do most of my work in but the average service and downstream transformers are typically 30%-40% loaded so neutral issues is not a problem.
The few cases where an overload neutral was an issue was on the secondary of a 208/120 Wye transformer that was at 90%-100% load.
We did have issues in the early days of UPS where there were mechanical governors, and no input filters on the UPS.
Additionally when VFD's were replacing motor starters years ago on large projects that had single transformers dedicated to mechanical loads, there were issues with the utility transformers and early generation electronic relaying.
But most harmonic issues I see are not harmonics but typically hardware issues, grounding issues, such as neutrals grounded downstream of the transformer compounded by other wiring issues.