roger said:Doesn't matter, the shortcut provides the correct answer.
True, but I don't see that this is a shortcut.
roger said:Help me out here and walk us through this statement.
If you do this calculation with pencil, you are forced to do two calculations, and the units of the intermediate result are correct. However, if you do this with a calculator, you have to press an extra key to see the intermediate result which is unnecessary.
roger said:The non-existent voltage is taught as a shortcut in many instructional courses, so it may only be confusing to you..
I am nitpicking the use of the word "shortcut" here.
roger said:I monitored voltage on a feeder at a hospital last month and had over 8,000 voltage changes in a 24 hour reading, so how long would one need to wait for the system stabilize to give us more than an approximate?.
My point is that this is not a matter of accuracy. Every measurement you make may be very accurate. The fact that the readings change often does not change the accuracy. I think stability would be a better term.
roger said:And where is the wrong one in this thread?.
Nothing truly wrong here, mostly nitpicking, but I still think you are wrong about the 200A line to line current. You have combined two equations, each of which is numerically correct, but not as a combination,
166,200w / 480v = 346.25a / 1.732 = 200 amps phase to phase
Furthermore, your result is wrong, the line current cannot be equal to the line to line current in a balanced system.
Pa = Vline x Ipp x 3
Ipp = Pa/(Vline x 3) = 166,200VA/(480V x 3) = 115.4A, or
Iline = 1.732 x Ipp = 200A