The drawing in post #5
Lou,
I was under the impression that this was a 208Y/120 volt system not a single phase 240 volt system. If so that diagram would not apply.
The drawing in post #5
Lou
I also think it would be 104 or half, maybe someone check it out for us?![]()
However if you bond your new neutral point to ground you will create a short circuit (there is a 16V difference between the input and output side L-G).
Ron,
What is the system voltage that you're asking about? We're getting all different conflicting information making it impossible to properly answer the question.
Jim,
How would the current flow on that short circuit (keep it simple {if you can} please).
If you are bringing in 2 phases from the 120/208 3? system, without the neutral, grounding the center point of the transformer winding will make a connection through the earth to the neutral. This will produce unstable voltages and is an NEC violation. The legs would be 120 volts if there were a solid metallic connection to the 120/208 neutral point, but 104 volts if there were an infinite resistance through the earth.
Here is the circuit instead of a single phase 120/240 volt transformer.
![]()
My 'guess' is if you didn't ground XO, you would have 104-volts. If you did ground it, you would have 120-volts with the ground path being a CCC.
Does that cc mean you won five bucs and are going to cc's or what?![]()
The 'teaser' is what happens if you try to do the same thing using the secondary of a three phase transformer.
Jim and Jon
I was really thinking along the lines of a single core 480/208 delta wye dry type transformer.
I still believe the voltage would be 104 volts with single core, three phase or single.
it would act like a voltage divider I think.![]()