Aren't most the dry type Transformers use to convert 480/277 to 208/120 of the single lamination type?
Not being an expert in transformers I don't know how much magnetic isolation there is between the phases
this could have an effect on the difference between a single and a three phase being used the way I show them?
If the three primary-secondary pairs were genuinely wound on a single core, there would be no wat to have three separate phase timing waveforms; they'd be locked into a single sine wave.
A 3-phase transformer has three separate cores bolted in to a single frame, but the three winding pairs are not electromagnetically coupled to each other. They are effectively three individual units.
Here's why it matters (and please remember this is from my grasp of how things work, and not formal education):
Two 120v windings in series will function fine as a voltage divider if on a single core, because the electromagnetic function locks them together in the voltage-per-turn ratio sense. That's how center-tapped secondaries survive load imbalances. If fed 240v, the output would be 120/240v; if fed 208v, the output would be 104/208v, as expected.
Two 120v windings on separate cores in series would suffer the same issues as an open-neutral condition in a service: the voltages on each side of the 'neutral' would vary with load shifts. The volts:turn ratio would not be locked between them. With only line-to-line loads, the center tap would measure as expected.
Now, if we connect the transformers' 'neutral' point to the source's neutral, we'd better make sure the single-core/separate-core situation matches the source. If we connected two windings on a single core two a 208/120v source, all kinds of evil will happen. Two separate transformers (e.g., 2/3 of a 3ph unit) are required.
If the source is single phase, then the connection to the source neutral is "optional" with a single-core-sharing pair of windings, but mandatory if there are separate cores and you want the center-tap's voltage to be stable, and not floating as I described above.
So, using the 2/3 of a 3ph unit, you'd measure 104v with the neutral floating, and 120v with the neutral connected. The former would be useless as a source, but the latter would basically be in parallel with the 2/3 of the source power supply. The circuit impedance would be all that keeps transformer differences from creating more evil.
So, how'd I do? :smile: