Yes, you need E stop/panic button
A public pool I built in NJ in 2012 required it. Must be visible.
Local rule? 680.41 does not specifically require E stop/panic button, just a way to shut down the pump(s) that is clearly identified and with certain vicinity of the spa. E stop/panic button type of control may be the most commonly chosen method though.
 
Local rule? 680.41 does not specifically require E stop/panic button, just a way to shut down the pump(s) that is clearly identified and with certain vicinity of the spa. E stop/panic button type of control may be the most commonly chosen method though.

In GA, it’s part of the pool construction code.


Sent from my iPhone using Tapatalk
 
In GA, it’s part of the pool construction code.


Sent from my iPhone using Tapatalk
That from NFPA, IBC, etc. or something local?

Since this site primarily about NEC - NEC doesn't require E-stop/panic type device, other codes or amendments could still apply in some places though.
 
That from NFPA, IBC, etc. or something local?

Since this site primarily about NEC - NEC doesn't require E-stop/panic type device, other codes or amendments could still apply in some places though.

2018 ISPSC

Int’l swimming pool and spa code


Sent from my iPhone using Tapatalk
 