I have space heater within same room as the panelboard from which its fed from.
The panelboard circuit breaker is within sight from heater.
I see NEC 2017 section 424.19 first paragraph says the disconnecting means specified in 424.19(A) and (B) must be lockable
However in actual NEC 2017 section 424.19(A) or 424.19(B) says disconnect or be within sight or lockable open.
So should the breaker in panelboard be lockable open or within sight is sufficient.
The panelboard circuit breaker is within sight from heater.