Can you take a 100A main breaker panel, remove the main breaker, install a 200A main breaker (same brand) and run 200A through the panel???
Square D Homeline 125A 30 space panel and
Square D Homeline 200A 30 space panel are identical except for the breaker size. All the busses are the same, grounding bars are the same, etc. Where can I find on the name plate or spec sheet if upgrading the breaker is acceptable on certain panels? I have not been able to find anything on Schneider website that prohibits it, but I am not convinced.
Square D Homeline 125A 30 space panel and
Square D Homeline 200A 30 space panel are identical except for the breaker size. All the busses are the same, grounding bars are the same, etc. Where can I find on the name plate or spec sheet if upgrading the breaker is acceptable on certain panels? I have not been able to find anything on Schneider website that prohibits it, but I am not convinced.