Hi All,
I have been reading up on splicing service cable and feeder cable. I was curious if the splices needed to be irreversible or not. The only wiring, I can find, that needed to be irreversible is the GEC. If you splice into it. So if I am reading the code correctly, you can use split bolts. 230.46 and the the articles it refers you to say nothing about irreversible splicing. Is this correct?
Thanks,
Jim
2014 NEC
I have been reading up on splicing service cable and feeder cable. I was curious if the splices needed to be irreversible or not. The only wiring, I can find, that needed to be irreversible is the GEC. If you splice into it. So if I am reading the code correctly, you can use split bolts. 230.46 and the the articles it refers you to say nothing about irreversible splicing. Is this correct?