AlWired

Member
With regard to a split system A/C system (heat pump outside and air handling unit inside), would it be a fair assumption to say the heat pump complies to Article 440 while the air handling unit complies to Article 430?

Thanks in advance.
 
I have always considered the AHU for a mini split system to fall under 422 Appliances. I sure there are varying opinions.


As some of the AHJ in my area require a separate disco and some don't. I now just call the inspector ahead of time and ask. Although I feel it falls under 422.31
 
he might not be asking about a mini split, but just a normal split system. I think they fall into different categories.

WooHoo! Post 500! I'll catch up with Bob someday!! (at this rate, long after we're both dead though)
 
jerm said:
WooHoo! Post 500! I'll catch up with Bob someday!! (at this rate, long after we're both dead though)

Perhaps you will in the next century, but by then he will have at least 50 billion or so posts. :D
 
iwire said:
Mini system or not the NEC requires some sort of disconnecting means at the indoor unit.
Which is sort of a pain to do, sometimes. Something that could be done at the factory for a couple bucks costs a couple hundred, sometimes, to pull off in the field. I havn't looked into it thoroughly, but I suspect a breaker lockoff might be the thing to do.
 
peter d said:
OK, strike that, I have seen them. :D

In residential I never have though.
Then you must not have seen any of my work? :D I usually just put a Wiremold V5747 with a snap switch right next to the indoor piece. Very darned few of these have a factory rocker switch, and that's a shame. Two dollars at the factory could save a whole lot of aggrivation. Particularly now that they're making mini-splits that you can hang 20-32 indoor units off one outdoor unit, for refitting old office buildings and such.
 
stickboy1375 said:
I swear the last split unit I did the indoor blower was low voltage...?

mitsu makes a minisplit that has 12v fans indoors. They're really quiet. The included IR remote is nice too.
 
For the mini-splits I have done, we bring the HR outside to a SP or DP switch then feed the unit. The wiring from there back to the inside unit is usually LV.

There have been a couple of units where we have had to run wire from outside/inside. There are usually 5-7 wires I don't know where you would find a 5 pole switch.

On one occasion, we had to re-run 7 #14's 150' from the inside unit to the outside unit because the signals on the couldn't "travel" through the splices in the 3 or 4 junction boxes along the way. (That was a fun pull.)

The point is a disco by the inside unit may cause a unit to not operate properly.
 