Ok, so far we have the following violations:
1: A #12 double-lugged onto that 50/60 amp breaker with no supplemental OCP;
2: No grounding electrode at structure;
3: No conduit bushings;
4: Equipment grounds not connected;
5: Romex used in wet location;
6: Possible burned buss stab;
7: Code Section 334.30 violation (Anyone care to spell that one out, my 1999 NEC doesn't have that section...)
was that # 12 for the pump relay?
I have seen that many times in inspected work in southern Oregon!
Even if it was that still doesn't make it right.
But the main thing that caught my eye was the #12 lugged into that 50 amp breaker. After reviewing this thread and looking at the video again, I do see all the other issues here as well.
Yikes.