Q10. Does the Code require bonding around raceway knockouts for 120V, 208V, or 240Vfeeders and branch circuits?
Q10. All metal parts intended to serve as the effective ground-fault current path, such as raceways, cables, equipment, and enclosures must be bonded together to ensure they have the capacity to conduct safely any fault current likely to be imposed on them [250.96(A)]. If the knockouts are damaged, the integrity of the fault current path is jeopardized and must be bonded around. If the knockouts are not damaged, no extra bonding is required.
Q11. Does the Code require bonding around raceway knockouts for 277V or 480V feeders and branch circuits?
A11. Metal raceways or cables, containing 277V or 480V circuits, terminating at ringed knockouts must be bonded to the metal enclosure [250.97] with a bonding jumper sized in accordance with Table 250.122, based on the rating of the circuit overcurrent protection device [250.102(D)]. A bonding jumper isn?t required where ringed knockouts aren?t encountered, or where the box is listed to provide a permanent and reliable electrical bond [250.97 Exception].
This is why I was thinking that the Offset Nipple would not require an extra bonding jumper if all of the KO's were removed. I didnt know it was different for a service than it was for Feeders or Branch Circuits.