Why not post a code reference<
Because I was reading about bonding bushings.
Why not post a code reference<
So following that logic - one would need to be a premidonna to be a Foreman? :grin:No your not "anal" IMO. Now you might be guilty of being a electrician though.
![]()
Read 230.82(2) as well....Because I was reading about bonding bushings. :roll:
200.7 - no exception for the pictured application.Why not post a code reference<
No comment:I guess if we all kept our opinions to ourselves and the NEC to our posts, we would have nothing to talk about.
So following that logic - one would need to be a premidonna to be a Foreman? :grin:
If you mean to say you're a Foreman? That doesn't make your "smarter" - right or wrong - that makes you "In Charge", and "Under-paid"....So your saying I might not be smarter than everyone else on the
crew? I'm going to have to disagree!![]()
IMO there is nothing to imply "One End"
The wording 250.64E used to be 250.92(A)3 until Mike Holt got a hold of it in the '08 cycle.... His reasoning for moving it was to move it to a location better suited to it - for the application of GEC's.
It is absolutely implied. The specific requirement to bond both ends of a metallic raceway that encloses a GEC is not present anywhere else.IMO there is nothing to imply "One End"
I will also point to the wording of 250.90, and the fact that the first word of 250.92(A)2 is "ALL". As well as the wording of 250.92B - note that the the use of plaruals for raceways, and enclosures. If the meter in this case were a raceway (gutter) it would definatly need to be bonded - would it not? The fact that it has an additional MBJ in it should go back to 250.90 for additional reinforcement.
Is anybody bothered by Solid White Wires made up on breakers? Am I just anal?
So which one do you bond it to???? Both have a MBJ. Both are service equipment enclosures.
Anyway - I would really like to know where the "one end" comes from? Nothing in the code to imply 'one end' is acceptable, (Other than a graphic from Mike Holt) or not. Especially, since this conduit or others like it will be current carrying.
And I too for you Bob, but don't think it is because it is solely because it has been the way I have been doing as a reason. Solely because I do not see how the imposed objectionable current is going to ignore the laws of physics and go the other way on a parallel path. It is going to go through that metalic path no matter how the code is written or how anyone of us interpets it. And I beleive it will be carrying roughly 50% of of the unbalanced neutral current from the main to the meter enclosure - would you disagree with that? And the method of doing that safely is laid out in 250.6 A&B, as well as 250.(A)4 - unless that becomes a non-metalic ot isolated at one end, I do not think that it conducts current safely, or provides a good fault path to the source - that is in the meter.But more importantly there is nothing that requires both ends or that the conduit must be connected to the neutral twice.
Mark I have a great deal of respect for you but I really think your just stuck on 'we have always done both ends so it must be right' line of thinking.:smile:
If anything I think a lot of other people are ignoring that this is current carrying and bonding one end is not going to change the direction of that current - bondint it on both ends is a much safer method of carrying that current - essentially making the enclosures 'one' to handle the current imposed.
You think that bonding one end is going to MAKE current NOT go through it in any way shape or form? It's going weather you like it or not and at the same levels until the resistance of of the connections is changed - since resistance in this case can only go up - a higher resistance connection on this would be shown in the form of heat.... Please take a look at 250.6(B)4 bonding both ends falls into that.... Otherwise get the poco to change metering rules to remove the second ground point, or remove the MBJ, or non-metalic fitting beween the two.And you are ignoring the fact that this bonding is required to conduct safely any fault current likely to be imposed.
I do see the point you are making. However, I would rather make it more difficult for the neutral current to travel on the conduit. I want it to travel on the neutral conductor.
You do realize that your method increases the neutral current on that conduit? Your method cannot be called safer.
You think that bonding one end is going to MAKE current NOT go through it in any way shape or form? It's going weather you like it or not and at the same levels until the resistance of of the connections is changed - since resistance in this case can only go up - a higher resistance connection on this would be shown in the form of heat.... Please take a look at 250.6(B)4 bonding both ends falls into that.... Otherwise get the poco to change metering rules to remove the second ground point, or remove the MBJ, or non-metalic fitting beween the two.
OK, so if one end is not well bonded and has a high resistance connection, and that connection is in parallel with the well bonded, low resistance connection at the other end, will the high resistance connection carry enough current to cause problematic heating? I think we can treat this as a constant voltage source, unlike a high resistance connection in series, where all the current goes through the high resistance connection. So then P = V^2/R, and the high resistance connection will be dissipating less power than the low resistance connection.You think that bonding one end is going to MAKE current NOT go through it in any way shape or form? It's going weather you like it or not and at the same levels until the resistance of of the connections is changed - since resistance in this case can only go up - a higher resistance connection on this would be shown in the form of heat....
Now before I let this thread die its horrible death.I agree that the best solution is to use a non-conducting raceway between the two enclosures.
Cheers, Wayne