kiss

Senior Member
Square D 225 Amp panels with MLO or feed thruu panels come with an oblong lug at the nuetral and on some panels for phase lugs. Square D states that the oblong lug can have 2 wires under the same lug. Reading 408.21 in the 2002 NEC tels me otherwise. The wires under this lug are not parallel conductors, but the second conductor is a tap for a secondary section of the panel. Any help on this is appreciated.
 
Re: Square D panel lugs

In My opinion 408.21 is black and white.

One terminal, one conductor, regardless of the terminals listing.

Unless it is for parallel conductors.
 
Re: Square D panel lugs

Does that mean that on the phase lugs you can put as many wires as you can fit under that lug? or 2 wires of the same or different sizes as you would if making a tap? Is there anything in the 2002 NEC pertaining to phase lugs or just at the neutral? Also whats the difference wether its the phase lug or the neutral lug? Slightly confused.
 
Re: Square D panel lugs

The handbook has a long explination about how it is a trouble shooting problem to have to disconnect the grounded conductor for a second circuit (which may remain live) at the same time the grounded conductor for the first circuit is bing removed. It also notes that some panelboard instructions permit the use of a single conductor termination for more than one equipment grounding conductor.

So it is basically saying that two wires may be OK for EGC's, just not neutrals.

Personally, I'm thinking about the danger of disconnecting a neutral for a Multiwire branch circuit while that circuit is still hot.

Steve
 
Re: Square D panel lugs

P.S. That also explains the exception for parallel neutrals. Only one circuit, no greater danger of accidently disconnecting the neutral from a different circuit.

Steve
 
Re: Square D panel lugs

Hey guys what happened to the manufacturer states it that makes it a okay. For eons of time SQUARE D legally was and is allowed to double lug cbs due to it having two lugs per attachment point.
Read the manufacturers specs. Tey do override the code in many circumstances. Square d has been in court with many jurisdictions and always win the case. So listen and learn from time honored procedures. :p
 
Re: Square D panel lugs

Originally posted by straps:
Read the manufacturers specs. Tey do override the code in many circumstances.
Can you show us an instance where the manufacturers specifications lessen the NEC?

You are talking about the terminals on a breaker and in most instances you may use a terminal per it's listing...unless there is a specific NEC section that prohibits it, like this one.

408.21 Grounded Conductor Terminations.
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.

Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.
 
Re: Square D panel lugs

Straps,
For eons of time SQUARE D legally was and is allowed to double lug cbs due to it having two lugs per attachment point.
what does that have to do with this post which is talking about 408.21 and not the lugs on the circuit breaker?

BTW, the oblong or figure 8 lugs are not double barrel as in two lugs.

Roger
 
Re: Square D panel lugs

Straps Square D still makes them and it is still code compliant to put two wires on them. But this thread was about the neutral bars.

By Kiss: Square D states that the oblong lug can have 2 wires under the same lug.
I had some literature for mill bank meter sockets that said the same thing for there oblong lugs. But they don't use them any more. They now use set screw. :(
 
Re: Square D panel lugs

Again I will ask my question [/QUOTE]( Does that mean that on the phase lugs you can put as many wires as you can fit under that lug? Is there anything in the 2002 NEC pertaining to phase lugs or just at the neutral? Also whats the difference wether its the phase lug or the neutral lug?) Removing the neutral wire under load from the oblong lug would create a problem not just in the second section of the panel, but the first section of the panel as well. Never mind the problems you will have if you have common neutrals on your branch circuits by loosening the neutral lug to remove the neutral. But from what I am reading in the replies is that this is O.K.
I wonder if there are any other panels out there that have this type of lugs on the panels? Phase lugs or neutral lugs? I have not seen any.
 
Re: Square D panel lugs

Kiss, these lugs are common. The number and size of conductors allowed to be used with them are stamped on the lug. Read articles 408.21 (per your first post) and 110.14(A) for the answer to your question/s.

Roger

[ December 02, 2004, 09:40 AM: Message edited by: roger ]
 
Re: Square D panel lugs

Posted by Kiss:
Does that mean that on the phase lugs you can put as many wires as you can fit under that lug? Is there anything in the 2002 NEC pertaining to phase lugs or just at the neutral?
In general, you can put the number of wires the lug is listed for on it. If it is listed for 1, then one wire only. If it is listed for 2, then 2 is OK.

Also whats the difference wether its the phase lug or the neutral lug?)
If you are going to take off a phase wire, you will probably shut off the breaker first. If not, and you pull both wires off, you are still only disconnecting power to both loads. Not the same problem as pulling off the neutral of a multiwire branch.


1st post by kiss:

but the second conductor is a tap for a secondary section of the panel.
If it is a neutral conductor, it is a violation. It should be on its own lug. If is is an equipment ground, it is OK.

Steve
 
Re: Square D panel lugs

It's clearly a NEUTRAL WIRE. It's on a oblong lug thats provided with the panel and there is no provision to put a second wire to feed a second panel ( feed thruu ) in any other lug that would fit a # 3/0 wire.
 
Re: Square D panel lugs

This sounds like a typical situation where someone is learning that manufacturers can build and UL can list products which cannot be installed under some editions of the NEC.
Also the Square D lug is more of a figure eight than an oblong/oval, so maybe it can be considered as two openings.

But, the answer is: just because it is possible does not make it acceptable for installation unless approved by the AHJ.
 