Square D 225 Amp panels with MLO or feed thruu panels come with an oblong lug at the nuetral and on some panels for phase lugs. Square D states that the oblong lug can have 2 wires under the same lug. Reading 408.21 in the 2002 NEC tels me otherwise. The wires under this lug are not parallel conductors, but the second conductor is a tap for a secondary section of the panel. Any help on this is appreciated.