Is the UL Listing of the panel void if you replace the main breaker with a new UL listed square d breaker?
UL does not have a problem when there is a 'like with like' replacement. For example, replacing a faulty 100A main breaker with another 100A main breaker is simple maintenance.
Things start getting fuzzy when you do more than that, or start changing the question. An example is when you retrofit fluorescent fixtures: UL expects you to replace the ballast .... but change the ballast from T-12 to one for T-8 bulbs, and suddenly UL wants you to use a listed 'kit,' and objects to your simple ballast swap out. Their position will be 'that's not the fixture we tested.'
As for 'voiding the warranty,' there's a lot to be said for the role of honesty in relationships. Some folks are less honest than others; just try collecting on the 'lifetime warranty' of a few different brands of screwdrivers, and you'll see what I mean. One firm will replace the tool with no questions asked, while another will require that their rep look at it and try to find a reason to decline the warranty claim. Electrical parts makers are no different.
I've seen junk of all kinds with UL labels, ...
A UL listing simply says that something was built to a certain set of specific standards.