If I'm running 2 hots, 1 SSBJ, 1N and 1G from secondary side of xfrmr to a 2P disconnect switch where would the SSBJ land in the disconnect switch?
If I'm running 2 hots, 1 SSBJ, 1N and 1G from secondary side of xfrmr to a 2P disconnect switch where would the SSBJ land in the disconnect switch?
Wouldn't the "G" mentioned BE the SSBJ?Connected directly to the switch enclosure via lug or an EGC bus if there is one.
Yes. I missed that "G" part.Wouldn't the "G" mentioned BE the SSBJ?
Thank you.Yes.
Yes
They you would have one wire more than you need. Just confirming that you got the upshot of post #3.If I'm running 2 hots, 1 SSBJ, 1N and 1G from secondary side of xfrmr to a 2P disconnect switch
I wasn't aware the ground could be the SSBJ. Thank you.They you would have one wire more than you need. Just confirming that you got the upshot of post #3.
Cheers, Wayne
Basically the EGC and the SSBJ perform the same function. So they are just different names for the same thing depending on whether it is upstream or downstream from the first OCPD on the supply system. Because the EGC sizing rules are based on the size of the upstream OCPD, and so they can't apply upstream of the first OCPD.I wasn't aware the ground could be the SSBJ. Thank you.
Another reason for the distinction between the two is that the SSBJ is usually larger than the EGC on the load side of the disconnect.I wasn't aware the ground could be the SSBJ. Thank you.