I have made a true and exact statement that can be confirmed with an ammeter. To explain would be outside the scope of this forum but I think you already understand.Mike, that is a falsehood and I have no idea why you persist in stating it.There is no existing parallel path where the neutral and equipment grounding conductors are intentionally bonded on both ends.
And this connection will have little or no current unless something goes wrong which would lead into the discussion of a non-compliant installation.No Mike, it is not just a connection via dirt, it is connection via aluminum or copper conductors. And this parallel path exists in a correctly installed and operating system.What is trying to be construed as being parallel paths is the connection of different systems to earth. The only way this poses a danger is if something goes wrong with one system or the other.
Unless you are saying that the electrical utility and the cable is the same system then I would tend to believe that they are two separate systems.Which is exactly the case when a coax shield is tired into the AC system.What is being discussed here is the intentional connection of two conductors in one system.
See the many post concerning the bonding of the EGC and the neutral from the generator to the premises wiring system that shows that the same amount of current will be present on both conductors at the same time. Now with the deepest of respect I ask you to show me where the same amount of current will be present on the shielding of the cable service as on the neutral of the utility service. This is why my comparison to the moon and the sun, both shed light but one is much brighter than the other.I disagree and you have yet to show why it is different other than you would like it to be.The comparison of the two is like comparing the New Moon to the Sun