What I have here is one of our 100 hp VFD's went out. Currently it is powering a 108 hp motor. I would like to get a larger VFD for this configuration but it is on a 125kva transformer.
My question here is what is the standard practice in sizing the two? I'm sure there is nothing wrong with having a larger transformer than the VFD, but is there anything wrong with having a larger VFD than transformer? I am thinking that I can just set the overloads on the VFD at around 150A but always think that the next guy in there can raise it up some time down the road for what ever reason and blow the transformer if the pump and motor gets stuck.
So is it standard to just size the transformer larger than the drive?
Here is how the power goes:
480V MCC > 100 hp VFD > 125kva isolation step up transformer > 108 hp, 1775v, 39A motor.
Transformer ratio 1910/480= 3.98* 39A= 155A@ 480v* 120%= 186A
My question here is what is the standard practice in sizing the two? I'm sure there is nothing wrong with having a larger transformer than the VFD, but is there anything wrong with having a larger VFD than transformer? I am thinking that I can just set the overloads on the VFD at around 150A but always think that the next guy in there can raise it up some time down the road for what ever reason and blow the transformer if the pump and motor gets stuck.
So is it standard to just size the transformer larger than the drive?
Here is how the power goes:
480V MCC > 100 hp VFD > 125kva isolation step up transformer > 108 hp, 1775v, 39A motor.
Transformer ratio 1910/480= 3.98* 39A= 155A@ 480v* 120%= 186A