The existing transformer survived unless I'm mistaken. And 125kVA would seem more than adequate.
The motor is 100hp/75kW. Again, it survived unless I'm mistaken.
So, I don't see any justification for upgrading either.
The drive worked for five years before it failed (from what cause we don't know) so one might assume it was fit for purpose.
So again, I don't see any need for an increase in rating.
Unless something has changed on the process side that we don't know about - then all bets are off.
You see no reason
I see a possible reason based on partial information
need drive mfg/pn
The moor is 108 HP unless a typo
afaik the drive has not failed?
drive is running at 140 A (at the limit for many 100 hp drives)
I'm surprised you did not ask how long it had been in operation?
As I said the xfmr may be fine if designed for this use
why do you like selectively chopping my posts up to distort their context?
so you can 'correct' me
load/xfmr = 140/150 = > 93% ignoring losses
not sure 'more' than adequate
if based on motor fla >95% 120 kva/125 kva