Hi everyone I just joined this forum. Appreciate any help on this question.
I have a customer who has a 208-230/3/60 30ton air cooled chiller
fed from one 200amp nonfused disconnect.
This disconnect line is protected by a 175 amp breaker.
My question is; can I install and feed a identical standby Chiller
from the same 200amp disconnect? Of course I would install double barrel lugs
on the load side of disconnect to feed both chillers. Each chiller has its own
built in disconnect means.
the main line from 175amp breaker is 2/0 thhn, the line to the
chiller is also 2/0 thhn.
Only one chiller will be turned on at any given moment.
Chiller will be permanently labeled “only use one chiller at a time.
The 200amp disconnect next to the chiller will be labeled MAIN cause
each chiller has its own factory mounted disconnect. Personnel will be trained
limited to operation of chillers.
Does this look doable? I can’t find any code that states otherwise. I did notice
some area in the 400 series code section where there was some suggestion that if
personnel is trained there could be some exceptions.
Gen info:
30 ton 208-230/3/60
rec over current 150 amp. MCA:125amp MOCP: 175amp.
Appreciate any info or guidance.
Gen info:
30 ton 208-230/3/60