MEP Guy said:Is anyone aware of a Code provision prohibiting the installation of a Standby Generator Transfer switch on the service entrance, prior to the main circuit breaker. The transfer switch would be rated as Service entrance equipment.
Thanks for any help.
I spoke with an inspector about a simular situation a few weeks ago and as an altenative method, he would like to see a grounding electrode conductor brought from the inside equipment, but it was redundant to the equipment ground ran with the feeder conductors.The main was located outside prior to the ats.This is a must.Grounds and neutrals were kept seperated after the ats.You will need to watch your main bonding location so as to not have your grounds carrying current.MEP Guy said:Thanks for the response ... the ATS is being cut into the existing elec system ... any problem with locating the ATS outside (Nema 3R) and running a service ground back to the existing service entrance equipment.
Thanks again.
bugzapper said:We've installed dozens of standby generators and transfer switches. A service rated transfer switch is always put before the main when used with pad and trailer mount generators.
MEP Guy said:Thanks for the reply - why is it a must to have the main before the ATS ?
Like i said before, 230.94 could be your main problem.Does your ats have a main?MEP Guy said:Any code problems ?
I would agree that you need to run an equipment ground with your feeders and seperate your grounds and neutrals in the load panel.Make your main bonding jumper in the ats.If you establish a grounding electrode system out at the ats,You can look at the building as a seperate structure and bond your existing electrodes in the building to the equipment ground bar.MEP Guy said:Agreed?
RUWired said:I would agree that you need to run an equipment ground with your feeders and seperate your grounds and neutrals in the load panel. Make your main bonding jumper in the ats.
If you establish a grounding electrode system out at the ats,You can look at the building as a seperate structure and bond your existing electrodes in the building to the equipment ground bar.
Rick
MEP Guy said:So we can just just run a seperate electrode grounding conducter from the ATS to the existing grounding system without seperating the gounds and nuetrals at the existing service entrance because this be parrallel paths to ground ?