.... Am I missing something?
Okay - not being facetious this time. Just design issues - but only if they are interested in it running. If they are okay if it doesn't run then the circuit is okay.
For the following example I'm using 480V as a per-unit. On the 420V side, the currents will coorespondingly (is that a word?) scale higher.
Table 430.250 motor FLA = 40 A. LRA is ~ 240A
Transformer primary FLA = 36A. 125% x 36 = 45.1A round up to 50A. Normal motor CB is 250% x 40A = 100A
240A LRA on a 50A CB - hopefully it will trip regularly on startup.
Note on CB size: Yes, one can select a transformer Primary CB at 250% of Xfm FLA. If you do, then the secondary must be protected at 125%. Either way, the cb scales to 125% xfm primary FLA.
Then there is the voltage drop through the transformer. Figuring the xfm %Z = 2% to 5%, and the LRC is 6.7 X xfm FLA, the VD has to be horrendous. I didn't figure it, but you can. Suggest using a pf of .3.
Maybe is it is lightly loaded, it will start and run.
One other question: Considering the really odd motor namplate voltage is 420V, is the motor also 50HZ? That could hurt - it will definitely try to overspeed.
He calls himself a "technical solutions consultant"... I'm the third-party inspector who has to approve all the changes they made to get their equipment up to code
seriously - heart felt condolences
So this word, "approve", is that:
1. You promise the installation will work?
or
2. You promise there is no legal consequence? But, you make no guarantees concerning it working, or eventually (sooner rather than later) letting the smoke out of the motor or transformer.
Good luck with this one.
ice