MFRichardson16
- Charleston, SC
We have installed a 4160 volt Power distribution system on a airfield and are having power fluctuations once or twice a month.
Leaving the Airfield lighting vault with a 250 Amp 480 volt w/3-250MCM & #4 ground Feeder to a 3 phase (step up)150 KVA Pad Mounted 480/277Y to 4160/2400Y . The 3 phase 4160 volt system feeds 6- 25 KVA single phase pad mount transformer 4600: 240/120 single phase loads. The single phase transformers are spread out along 12,00 feet of airfield with the 3 phase 4160 system alternating two phases at each single phase transformer locations. We did not ground XO in the 150 KVA transformer due to past experience that it is a dead short across the 480v Side. Due to power fluctuations we talked to the ABB factory and the ABB factory engineer talked us into grounding XO/HO. When we turned power on did it destroyed the 250A 65KAIC breaker in the vault. So we went back to un-grounded XO/HO system. I have attached the transformer nameplates. The system has been since October but we are still having power fluctuations once or twice a month. Also in 4 or the remote sites the equipment are on UPS systems. The XO and HO are tied together inside the transformer under oil.
Why can you not ground XO/HO in the 150 KVA transformer?
What is causing the voltage fluctuations?
Will the 150 KVA Pad Mounted 480/277Y to 4160/2400Y work or should the transformer be changed to 480V Delta: 4160/2400 so we can ground HO?
Thanks in advance.
Mike
Thanks in advance.
Mike