That exactly confirms what I have been saying. The transformer isn't big enough.I am not ready to make that leap
the numbers indicate otherwise
motor at ~100%
xfmr at 95%
Can we leave it at that, please? Before the mods take a dim view.
That exactly confirms what I have been saying. The transformer isn't big enough.I am not ready to make that leap
the numbers indicate otherwise
motor at ~100%
xfmr at 95%
That exactly confirms what I have been saying. The transformer isn't big enough.
Can we leave it at that, please? Before the mods take a dim view.
Perhaps ambient temperature high limiting transformer output.we need to know how it was determined that output was limited
The transformer can saturate if voltage rises above its input voltage rating. A transformer is usually designed to operate near its saturation region. So any over voltage from pwm drive could damage it. But no over voltage from pwm drive as the transformer is not damaged.I'm just not sure if the transformer can saturate without raising input voltage? Does the pwm from the drive possible cause saturation? I like things that spin, not things that buzz and go pop! I'm just trying to learn from this.
Thanks
The sine filter is on the output of the drive.the filter ought to reduce any harmonics to negligible levels
If there is any asymmetry in the PWM output then it could cause saturation. That's why we used transformers with an air gap in the core design. I don't know if the output sine filter would reduce that possibility.Does the pwm from the drive possible cause saturation?
https://library.e.abb.com/public/a3be693a9ac8bf7bc125744e00339abe/ACS800_Sine_Filters_revG.pdf
page 35 might be helpful
xfmr S rating must => motor S rating
It can be assumed that the primary voltage of the transformer is about 10% lower
than the supply voltage of the drive because of the voltage drop in the sine filter and
the drive.
In other words a DC component from PWM drive.If there is any asymmetry in the PWM output then it could cause saturation
It's a possibility.In other words a DC component from PWM drive.
It's a possibility.
If it's lack of symmetry in the PWM waveform it won't be transient.That possibility could last but for a short time till the DC component decays to zero and the wave shape becomes symmetrical. So I think if the motor is switched on some time after the drive, issue due to any transformer saturation may be overcome, provided such a switching scheme is feasible.
Any illustrations please because I think only faulty equipment generate permanent asymmetrical wave form and associated even harmonics.If it's lack of symmetry in the PWM waveform it won't be transient.
If we could be absolutely certain that there was perfect symmetry we wouldn't go with gapped transformers. But we do.Any illustrations please because I think only faulty equipment generate permanent asymmetrical wave form and associated even harmonics.
If we could be absolutely certain that there was perfect symmetry we wouldn't go with gapped transformers. But we do.
One such was a pumping station in Yorkshire where we installed four 760kW VSDs that needed output step up transformers. So very similar rating to that of the OP which is why I picked thaat one.
This isn't an illustration. It is a real life example.
Which it doesn't appear to be.
This (from P39) is quite interesting and may be relevant to the issue:
If the transformer is receiving lower than rated input voltage, it will produce lower than rated output voltage.
It's a point Jraef brought up earlier.
The sine filter is on the output of the drive.
Harmonics are usually a consideration on the input side.