Hello,
I wanted to post a question on an issue we recently saw. Unfortunately I wasn't at the site so I have to take all the information third hand but here is what I know.
We sold a 875 KVA step up transformer to a customer to put on a SWD running a 1000 hp motor and yaskawa drive. The motor is 4160 volts and 122 amps, thus the step up transformer. They added a sine wave filter to the yaskawa drive. Yaskawa was rated at 1200 amps.
This is where I am losing info though. They said they were only able to get 840 KVA out of the transformer. I'm not sure where they were measuring, if they were reading that off the drive or taking measurements, I'm not sure on that. I found a similar motor online and used the numbers from it to get that it would take 788 kilowatts to attain full load. Now, the transformer is rated somewhere around a K-4 and with 100% being electronic load, it should probably be somewhere in the k-20 range. My question is this, has anyone seen a transformer not able to take additional loading like that? I don't believe they were increasing voltage to cause saturation. I've never seen it before, usually it just runs over temp. I've never seen it before and was wondering if anyone here had seen a similar experience. Either way, I believe they need a new transformer. But I wanted to get some information from anyone that could rationally explain the failure.