racerdave3
Senior Member
- Location
- Western Massachusetts
We have tossed this question around before, and as I read the code book I still have some questions about this. It has previously been discussed that a 2-2-2-4 SER cable must be protected by a 90 amp breaker (the SER cable is aluminum of course), and that table 310.15 (B)(6) only applies to the main feeder into the building (it states that a #2 wire can be protected by a 100 amp breaker). However, when you look at 310.16, both the 75 C column and the 90 C column list aluminum XHHW insulated wire. In the 75 C column it is listed as 90 amps and in the 90 C column it is listed at 100 amps. Now my only thought on this is that we are looking at the 75 C column because that is the rating of the equipment we are using?