jwelectric said:
(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s).The feeder conductors to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors. The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements of 215.2, 220.61, and 230.42 are met.
Understanding this section is easier than falling down. The sentence that is in bold and underlined above is the key to the whole section and does not allow the installation that is being mentioned concerning the AC unit.
To have a 30 circuit panel with a main breaker and then install a 100 amp breaker in the panel to supply another panel whether or not it is a lighting and appliance panel would not be a feeder that is between the main and the panel.
The feeders would have an overcurrent device that separated the feeders from the main and the panel; the 100 amp breaker would be between the main and the panel.
I could turn the 100 amp breaker off and not the service to the house. This section is clearly meaning that the feeders have to be controlled directly by the main service disconnect with no other overcurrent in between the feeders and the main.
In the first sentence it also states that if supplying feeders these feeders have to be the main power feeders to the dwelling unit. I don’t think that feeders supplying a second panel from the first panel would fit the description of the Main Power Feeders.
“The feeders would have an overcurrent device that separated the feeders from the main and the panel; the 100 amp breaker would be between the main and the panel.”
The service conductors [like tap conductors] are protected at their load end. . Feeder [& branch circuit] conductors are protected at their source. . Feeders will
always be separated from the main [service equipment] by an OCPD. . So by definition there will always be
2 overcurrent considerations before the feeder conductors begin. . Both functions [service conductor protection and feeder conductor protection] can be accomplished by a single OCPD or by separate OCDP. . As long as this is all within the service equipment enclosure(s), there’s no difference, the feeder originates from the service equipment either way.
The Article 100 definition of
Feeder says, “All circuit conductors between the service
equipment, the separately derived system, or other power supply source and the final branch-circuit overcurrent device.”
Service Equipment is “The necessary equipment, usually consisting of a circuit breaker(s) or switch(es) and fuse(s)
and their accessories, connected to the load end of service conductors to a building or other structure …..”
Feeders will can be separated from the main OCPD by a feeder OCPD. . That’s not going to impact the application of 310.15(B)(6).
You’re trying to single out the words “main disconnect” and apply that as meaning something other than the
whole of the service equipment. . But if that was true, you would have to more narrowly restrict the use of 310.15(B)(6)
farther than you have already.
If the main disconnect was a switch with fuses, you couldn’t use 310.15(B)(6) according to your reading. . The “main disconnect” is the switch and the feeder isn’t “originating” from the “main disconnect”
directly. . It could be feeders to separate dwelling of a multi-dwelling building, that wouldn’t matter. . According to your reading of the words “main disconnect”, they wouldn’t originate from the “main disconnect”. . They would be on the load side of a OCPD that would be positioned
after the disconnect [230.91]. . Even if it was one OCPD for both service and feeder protection.
If the main disconnect was a breaker and the feeder conductors were not large enough to be protected by that one breaker but needed individual lower amperage protection, you couldn’t use 310.15(B)(6) according to your reading. . There would be a feeder OCPD that would be separate from the “main disconnect”. . Once again, it could be feeders to separate dwelling of a multi-dwelling building, that wouldn’t matter.
“I could turn the 100 amp breaker off and not the service to the house.”
And that’s not an issue. . The 310.15(B)(6) wording adds
(s) for plural, “For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s).” . If this was talking about separate feeders to
separate dwellings, then it should have said, “For application of this section, the main power feeder shall be the feeder between the main disconnect and the lighting and appliance branch-circuit panelboards
for each individual dwelling unit.”
David