You realize that is a violation of the manufacturers instructions and therefore 110.3(B).
Well I do NOW
Are the instructions on the wire or the device ?
You realize that is a violation of the manufacturers instructions and therefore 110.3(B).
wireman71 said:I don't like stranded on screw connections.. Use crimp lugs of some kind..
j_erickson said:FWIW, MA has an amendment which would require you to make the stranded conductors solid if terminating them on wire binding screws. So th question in the OP is not OK in MA.
LarryFine said:I have found that I can keep the strands under the head of a terminal screw while tightening by pinching the loop closed tightly with the tips of a pair of needle-nosed pliers.
I do the same thing with even solid wire when tightening, for example, a grounding screw in a metal device or fan box, or a metallic enclosure or fixture housing. Try it! :smile:
Dennis Alwon said:And you have to keep the plate screws in a vertical position. :wink:
Mike03a3 said:If you mount the receptacle horizontally, do the screws also go horizontal or should they still be vertical? (I'm not actually mounting a receptacle, so this won't count as DIY advice.)
electricmanscott said:John the amendment says that "the terminals shall be identified for such use or the strands at the terminal shall be made solid"
I was under the impression that the terminals on receptacles were listed for stranded wire connections. What does this all mean??
racerdave3 said:I always use Stakons on stranded wire for my connections to devices. Maybe it costs a few cents more here and there, but in my mind it is the best possible installation and insures a solid connection
lordofpi said:Make sure to run a plumb line next to it to be sure though![]()
iwire said:Each stakon you install adds another possible point of failure.
But if you feel it's better to look good Stak-ons are the way to go. :wink:
iwire said:Each stakon you install adds another possible point of failure.
cschmid said:Just say no to solid wire..I need to figure out how to put solid in circle with line through it..the only solid I use is NM wire otherwise I use stranded on every thing That is in a pipe..terminateing is not a problem there are several types you can do..You can strip an inch twist it and put your striper back on wire and cut 1/4 inch and slide it just a Little shy of the end of the strip and fold around screw..you can use stak on fork terminals..you can by pre-made pig tails with factory crimp on them in white, black and green..Ideal sells them..you can buy back wire devices..So your options are many and when you have to work them in box or pull more wires in conduit you can with out fighting that nasty solid junk..
I used to have a guy who swore by left-hand twisting, but I'm hpelessly right-handed.LLSolutions said:I'm not a huge fan of it, but it's acceptable per NEC, when it comes up i leave the last bit of insulation at the end to keep it from becoming frayed.
I first learned about that idea a few years ago, and it does work well. Twist the strands up counter-clockwise. They tend to get more compact rather than splay all out when you tighten the screw. I really hate to put strands around a screw terminal anyhow, but sometimes you do what you gotta do.LarryFine said:I used to have a guy who swore by left-hand twisting, but I'm hpelessly right-handed.
Personally, I just pinch the loop shut with needle-nose pliers while tightening the screw.