Darksabre
Member
- Location
- United States
- Occupation
- Electrical Engineer
Hey guys - long time browser, first time poster :bye:
I'm trying to help a customer troubleshoot a 3-phase power system (specifically a reverse overpower protection relay - Basler BE1-32R). They are getting nuisance tripping from the relay, so I had them take readings of the line-to-neutral voltage and the current from the CT's going to the protection relay sense inputs. Whoever took the readings had equipment that could measure phase angles of the voltage and current, so they sent this data to me to analyze. Unfortunately, my 3-phase knowledge is not the best :happysad:.
I'm attaching the phasor diagram for easy reference, but basically, I'm concerned about how far out of phase Ic is from Vc.
I have no knowledge of their load characteristics at this point, but it looks like it is all over the place. Ia is leading Va by 81 degrees. Ib is lagging Vb by 33 degrees. Ic is...well...leading by 224, or lagging by 136...? I'm not sure what to make of that. Does the cause of this stand out to any of you 3-phase guys?
BTW, the reverse power relay in question operates by measuring voltage and current, and then calculating the phase shift. It uses that information to tell which direction power is moving, and then trips out if it is flowing in the tripping direction (with an adjustable Watt setting and Time Delay setting). An engineer was onsite to commission the relay by injecting a test current and recording the trip points. It seemed to perform as expected during the tests and tripped at the appropriate current flow. Could this odd phase shifting possibly cause the relay to be tripping?
Thanks guys!
-Aaron
I'm trying to help a customer troubleshoot a 3-phase power system (specifically a reverse overpower protection relay - Basler BE1-32R). They are getting nuisance tripping from the relay, so I had them take readings of the line-to-neutral voltage and the current from the CT's going to the protection relay sense inputs. Whoever took the readings had equipment that could measure phase angles of the voltage and current, so they sent this data to me to analyze. Unfortunately, my 3-phase knowledge is not the best :happysad:.
I'm attaching the phasor diagram for easy reference, but basically, I'm concerned about how far out of phase Ic is from Vc.
I have no knowledge of their load characteristics at this point, but it looks like it is all over the place. Ia is leading Va by 81 degrees. Ib is lagging Vb by 33 degrees. Ic is...well...leading by 224, or lagging by 136...? I'm not sure what to make of that. Does the cause of this stand out to any of you 3-phase guys?
BTW, the reverse power relay in question operates by measuring voltage and current, and then calculating the phase shift. It uses that information to tell which direction power is moving, and then trips out if it is flowing in the tripping direction (with an adjustable Watt setting and Time Delay setting). An engineer was onsite to commission the relay by injecting a test current and recording the trip points. It seemed to perform as expected during the tests and tripped at the appropriate current flow. Could this odd phase shifting possibly cause the relay to be tripping?
Thanks guys!
-Aaron