I was at a facility today aiding in some testing.
The facility has a group of four - 500 HP motors driven from VFDs. The problem is that the motor bearings are going bad very quickly.
GE took a motor back pulled it apart and determined that the bearings are 'fluted' which they say is an indication of current flowing through them. What has been found so far is 8 amps flowing through the EGC out to the motor.
I will try to describe the set up.
There is a dedicated 2000 KVA transformer feeding a 2500 amp 480 volt switch board, from the switchboard four feeders run to four Delta auto transformers then to the four VFDs finally out to the four motors.
The motors are outside and each motor has a 4/0 bare connecting it into a common grounding grid.
When an amp clamp is placed on any of these bare 4/0s and any single motor is run up we see 8 amps.
When I lifted the EGC from the motor that runs back to the VFD we lose the 8 amps.
Anyone have some ideas?
We are thinking induction as all the feeders on both the line and load side of the VFDs share a cable try system.
Any and all comments welcome.
The facility has a group of four - 500 HP motors driven from VFDs. The problem is that the motor bearings are going bad very quickly.
GE took a motor back pulled it apart and determined that the bearings are 'fluted' which they say is an indication of current flowing through them. What has been found so far is 8 amps flowing through the EGC out to the motor.
I will try to describe the set up.
There is a dedicated 2000 KVA transformer feeding a 2500 amp 480 volt switch board, from the switchboard four feeders run to four Delta auto transformers then to the four VFDs finally out to the four motors.
The motors are outside and each motor has a 4/0 bare connecting it into a common grounding grid.
When an amp clamp is placed on any of these bare 4/0s and any single motor is run up we see 8 amps.
When I lifted the EGC from the motor that runs back to the VFD we lose the 8 amps.
Anyone have some ideas?
We are thinking induction as all the feeders on both the line and load side of the VFDs share a cable try system.
Any and all comments welcome.