Re: Stray Current = Ruined Bearings
I'm not picking on you, Jim. But your post seemed as good a one to respond to as any other.
I don't think it is bad luck, and I think it is someone's fault. A VFD will, by its very nature, throw a bunch of harmonics into the system. They are going to travel through the bearings and into the shaft, unless you do something to stop them. They are going to cause damage, unless you do what a VFD manufacturer requires you to do. The "unlucky" ones who see the "rare" failures are the ones who did not put on the right bearings, or who did not properly ground the shaft.
The problem is well known. So too is the solution. Whose fault is it then? Well if this was an engineered installation, then it is the fault of the engineer, for not specifying the proper precautionary measures to go along with the VFD equipment. If it was installed by the plant personnel without any engineering, then it was the fault of the lead person in the electrical group.
Everyone should take notice: If there is a VFD, then you must take special actions to protect the bearings. Every time. No exceptions. Check with the manufacturer, and make sure your engineering consultant adds the proper lines to the VFD specification.
I am getting into this one a bit late (didn't check the Forum over the weekend). Also I didn't study the other site (from ccjersey's link). So I don't know if this is new information.Originally posted by jim dungar: Circulating currents in motor bearings is a known problem with variable frequency drives. It is rare but it does occur. . . . normally, it is not "someone's" fault as much as it is just bad luck.
I'm not picking on you, Jim. But your post seemed as good a one to respond to as any other.
I don't think it is bad luck, and I think it is someone's fault. A VFD will, by its very nature, throw a bunch of harmonics into the system. They are going to travel through the bearings and into the shaft, unless you do something to stop them. They are going to cause damage, unless you do what a VFD manufacturer requires you to do. The "unlucky" ones who see the "rare" failures are the ones who did not put on the right bearings, or who did not properly ground the shaft.
The problem is well known. So too is the solution. Whose fault is it then? Well if this was an engineered installation, then it is the fault of the engineer, for not specifying the proper precautionary measures to go along with the VFD equipment. If it was installed by the plant personnel without any engineering, then it was the fault of the lead person in the electrical group.
Everyone should take notice: If there is a VFD, then you must take special actions to protect the bearings. Every time. No exceptions. Check with the manufacturer, and make sure your engineering consultant adds the proper lines to the VFD specification.