Folks, please let me know if this is not the best forum for this thread.
In a very rural area with 7.2KV wye distribution (single phase plus neutral), I have measured low level magnetic fields almost 1/2 mile perpendicular the line that ultimately feeds about 50 homes with individual steel cased wells extending to the highly mineralized aquifer 400 feet deep. The fields don't fall off rapidly with square of the distance, which indicates to me that there is some current flowing back through the aquifer which is 400 feet deep.
In this area of 40 acre lots, each home has it's own single phase transformer, with the neutral distribution line jumpered to the secondary winding center tap.
To prevent the increase of this ground current, I'm thinking that new home's transformers should be configured as delta; using an overvoltage protector between the grounded secondary center tap (neutral) the primary neutral in case of a primary high voltage to secondary short. Thus each home site has essentially a separately derived neutral and no ground current will be generated except a small amount within that site between the grounding rods at the transformer, main meter panel, and well casing/pipe.
Since this seems like such an obvious solution to virtually eliminating stray ground current in rural settings, I'm wondering if I must be missing something. The only increased cost to the power co. is the overvoltage protection at the transformer secondary, and existing sites could be retrofitted over time without major wiring or transformer changes.
Anecdotally, I've rarely seen stray ground current problems (except on the local site) on Delta distribution systems, and homes in those areas without net current problems in house wiring will often have readings in living areas below 0.002 milligaus (yes, 2 microgaus) , the limit of my gear.
What am I overlooking?
Bruce
In a very rural area with 7.2KV wye distribution (single phase plus neutral), I have measured low level magnetic fields almost 1/2 mile perpendicular the line that ultimately feeds about 50 homes with individual steel cased wells extending to the highly mineralized aquifer 400 feet deep. The fields don't fall off rapidly with square of the distance, which indicates to me that there is some current flowing back through the aquifer which is 400 feet deep.
In this area of 40 acre lots, each home has it's own single phase transformer, with the neutral distribution line jumpered to the secondary winding center tap.
To prevent the increase of this ground current, I'm thinking that new home's transformers should be configured as delta; using an overvoltage protector between the grounded secondary center tap (neutral) the primary neutral in case of a primary high voltage to secondary short. Thus each home site has essentially a separately derived neutral and no ground current will be generated except a small amount within that site between the grounding rods at the transformer, main meter panel, and well casing/pipe.
Since this seems like such an obvious solution to virtually eliminating stray ground current in rural settings, I'm wondering if I must be missing something. The only increased cost to the power co. is the overvoltage protection at the transformer secondary, and existing sites could be retrofitted over time without major wiring or transformer changes.
Anecdotally, I've rarely seen stray ground current problems (except on the local site) on Delta distribution systems, and homes in those areas without net current problems in house wiring will often have readings in living areas below 0.002 milligaus (yes, 2 microgaus) , the limit of my gear.
What am I overlooking?
Bruce