Re: Stray Neutral Current along Wye distribution lines
Bennie and Rodger,
Thanks so much for the reference to the EC site and Scott. It really is a great resource.
Alas the text Bennie mentioned is not in print and I couldn't find a used copy online. Any suggestions for a currently in print text?
Scott,
Thanks for joining in. I looked at the zig zag transformer schematics on your references page. You really have done some fabulous work on the EC site. I've registered there and will definately spend some time there.
It looks to me like a zig zag is not something which would apply to a two wire distribution line of 10KV feeding a residential transformer. Or am I mistaken? Nor did I see any primary voltage short to secondary protection inherent to the zig zag.
I guess I'll have to talk with my local power co. supervisor to find out what primary to secondary short protection they are using on the existing two wire, 10KV distribution line which he mentioned was somewhere in this area.
Can you suggest an in-print text on power transmission for me?
Thanks!
C-H,
I think the SWER system would create essentially totally a net current situation, with magnetic fields falling off only linearly with distance. If SWER was used only for transmission over uninhabited areas, then only the wildlife would be affected. It seems a false economy (to save a second wire).
In Wye systems that I've measured, some "current mirror" effect is present; unless presented with a better path (like an aquifer or any conductor), a good portion of the ground current wants to follow under the lines. Alas, the effect seems pretty weak, and grounded wells seem to offer too good a path to the aquifer. It's unclear to me how the SWER ground currents will behave.
I think we're in different frames of reference regarding acceptable magnetic field levels. Ten foot per amp of net current will result in some pretty high levels. The line I've been looking at is estimated by Karl R. to have 8 amps of net current (based soley on my readings). I find the present magnetic field levels "acceptable" (10 microgaus) at over 1/4 mile (1320 ft). I normally see much faster drop off than I do along this line, and I'm not sure just yet why. Once the neutral line current is checked, I may know more. Another factor which I haven't determined is whether magnetic fields from above ground net current are as problematic for me (and hysterical cows) as ground current caused fields.
By definition SWER will create ground current levels substantially higher than even the MGN (Wye) system. Ground currents (despite quite low magnetic fields- levels that don't seem bothersome if from sources not flowing through the earth) seems to adversely affect both livestock and some people very profoundly. I don't believe the problem is unique to dairy farms in the US. Let's test it first in Sweden.
Interesting that Sweden has ground fault relays on the transmission lines. What is considered low voltage in your law relating to GF relays? I wonder if ground fault relays are used on HV lines here in the US?
Bruce McCreary