This is along the lines of this topic https://forums.mikeholt.com/showthread.php?t=195503 but I didn't want to hijack it.
This is actually a topic on another board. There are two attached town houses and both are fed from a single service line and regulator with a manifold supplying two gas meters. One meter for unit #1 and the other for unit #2. The outlet side of the meters go off to their respective units.
The problem arose when the owner of unit #1 was having a gas fireplace installed and the plumber, in disconnecting the gas line within the unit noticed a spark. This prompted him to tell the homeowner and call the gas company. Apparently there is an intermittent voltage of between 12-24V on unit #2s gas line after the meter was removed. I haven't been able to get an answer as to where that voltage was measured to from the gas line or what kind of meter was used. It very well may be that unit #1 us causing the problem. But the gas company did leave the meter for unit #2 disconnected and posted a turn off notice on the door indicating that the homeowner of unit #2 is to have an EC remedy the problem before they will re-install the meter. (It seems those people are out of town on vacation.)
My reply was that I don't think 12-24V would be unusual given that the gas lines in each unit is bonded to their respective neutrals and you are seeing much the same as the circulating currents on a common water service. I did say that I would check for a compromised service neutral but that's about it.
What do you think?
-Hal
This is actually a topic on another board. There are two attached town houses and both are fed from a single service line and regulator with a manifold supplying two gas meters. One meter for unit #1 and the other for unit #2. The outlet side of the meters go off to their respective units.
The problem arose when the owner of unit #1 was having a gas fireplace installed and the plumber, in disconnecting the gas line within the unit noticed a spark. This prompted him to tell the homeowner and call the gas company. Apparently there is an intermittent voltage of between 12-24V on unit #2s gas line after the meter was removed. I haven't been able to get an answer as to where that voltage was measured to from the gas line or what kind of meter was used. It very well may be that unit #1 us causing the problem. But the gas company did leave the meter for unit #2 disconnected and posted a turn off notice on the door indicating that the homeowner of unit #2 is to have an EC remedy the problem before they will re-install the meter. (It seems those people are out of town on vacation.)
My reply was that I don't think 12-24V would be unusual given that the gas lines in each unit is bonded to their respective neutrals and you are seeing much the same as the circulating currents on a common water service. I did say that I would check for a compromised service neutral but that's about it.
What do you think?