gar
Senior Member
- Location
- Ann Arbor, Michigan
- Occupation
- EE
100720-1241 EST
Petrosa:
Check the line to line voltage at the main panel. If the difference between the two is closer to 0 V instead of the expected 240 V, then both legs have the same phase relative to neutral. If both were the same phase, then a 5 V rise on both relative to earth would be more reasonable.
.
Petrosa:
Check the line to line voltage at the main panel. If the difference between the two is closer to 0 V instead of the expected 240 V, then both legs have the same phase relative to neutral. If both were the same phase, then a 5 V rise on both relative to earth would be more reasonable.
.