700.12(F) Exception permits a separate circuit if normal lighting in the area is supplied by three or more circuits. See the Exception for additional req'ts480sparky said:Is 700.12(F) what you're looking for?: "The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches."