I have a 200amp meter loop with a four space sub feed. If I sub feed a 100amp main breaker panel in a de-tached garage, do I need to bond the gounded conductor to the equipment ground bar or is it seperate at that point. It is bonded at the 200amp meter loop and there is no egc ran with the sub feed to the garage. I read 250.32 but still not sure where this fits in. I am thinking it needs to be bonded.
 
Re: Sub Feed Ground

If you meet the provisions of 250.32(B)(2), you must bond. In short, you treat it like a service and provide a grounding electrode system as well.
 
Re: Sub Feed Ground

Is this subpanel bonding this hard to understand or is it just me having a hard time with it?
 
Re: Sub Feed Ground

Samz, can you elaborate on the point in the process at which your confusion starts?

Do you understand why you shouldn't bond the grounding and neutral conductors twice (once @ service, and again @ detached building) unless there are no metallic paths between them? That is key, at least when I think about it. :)

Once the "whys" are understood, the "whens" and "whats" fall into place. :D
 
Re: Sub Feed Ground

As George pointed out the key here is metallic paths between the two structures. If none exist than you may eliminate the EGC between the garage and the meter loop. If a metallic path does exist, say as a phone line for example, than the EGC must be pulled and must be separate from the grounded conductor at the garage. This will prevent a parallel path for the current to flow on the phone line etc. The safest bet would be to simply pull the EGC with the feeder conductors and separate the grounded and grounding conductors at the panel.
 
Re: Sub Feed Ground

Originally posted by infinity:
As George pointed out the key here is metallic paths between the two structures.
....that are bonded to the grounding system in both buildings or structures.
 
Re: Sub Feed Ground

You're right Bob, they would need to be bonded to form a parallel path. And if they were properly installed than they would be bonded at both structures. I was making an assumption. Thanks for the correction.


Trevor
 
Re: Sub Feed Ground

Originally posted by infinity:
You're right Bob, they would need to be bonded to form a parallel path. And if they were properly installed than they would be bonded at both structures. I was making an assumption. Thanks for the correction.
Morning Trevor.

What I posted is part of 250.32(B)(2).

(2) Grounded Conductor. Where (1) an equipment grounding conductor is not run with the supply to the building or structure, (2) there are no continuous metallic paths bonded to the grounding system in both buildings or structures involved, and.... (
I think that many times "bonded to the grounding system in both buildings" is forgotten about when we talk about 250.32(B)

Not sure what you mean by properly installed. :confused:

A chain link fence between two structures is a continuous metallic path but is not usually bonded to the structures although it could be and that would make a difference.

Is a phone line bonded to both structures?
 
Re: Sub Feed Ground

Here's a graphic with some commentary from Mike Holts material.

1014156469_2.gif


This subsection added a new requirement and it reads:


(B) Grounded Systems
(2) Grounded (neutral) Conductor.
Where (1) an equipment grounding conductor is not run with the supply to the building or structure, and (2) there are no continuous metallic paths bonded to the grounding system in both buildings or structures involved, and (3) ground-fault protection of equipment has not been installed on the common ac service, the grounded circuit conductor run with the supply to the building or structure shall be connected to the building or structure disconnecting means and to the grounding electrode(s) and shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded.

The size of the grounded conductor shall not be smaller than the larger of:
(1) That required by 220.22 (maximum unbalanced neutral load), or
(2) That required by 250.122 (equipment grounding conductor size). Figure 250?10

Intent: The new sentence specifies how to size the grounded (neutral) conductor to a building or structure, when an equipment grounding conductor is not run to the separate building or structure.

Author?s Comment: When an equipment grounding conductor is not run to a separate building or structure, the grounded (neutral) conductor must be used to provide the effective fault current path required to clear any line-to-case faults in addition to carrying any unbalanced neutral current.


Roger

[ January 15, 2006, 09:40 AM: Message edited by: roger ]
 
Re: Sub Feed Ground

I do understand that if there was an EGC ran with the other conductors and both were bonded that the unbalanced load would be returning on any path including any metallic path that was bonded. Its just hard for me to understand why it wouldn't do ths same thing since it is bonded at the second service. Does it just on the path to the ground rod?
 
Re: Sub Feed Ground

Originally posted by Samz:
Its just hard for me to understand why it wouldn't do ths same thing since it is bonded at the second service.
What would the second path for neutral current be, if there were no other metallic paths?

If you pull an equipment grounding conductor with the outside feeder, you don't bond at the detached building. The path is:

Neutral screw of receptacle > neutral branch circuit conductor > neutral bar of subpanel > neutral conductor of feeder > neutral bar of service, where the grounding system is bonded and disappears as the current gets to > Transformer XO.

Does it just on the path to the ground rod?
If an EGC is pulled with the feeder, the grounding electrodes are connected to that, not the neutral conductor, in the detached building. So no neutral current will flow on the ground rod, since they are not connected together (in a direct sense).
 
Re: Sub Feed Ground

Some of the confusion here may be why there is a ground rod needed at the detached building. I know that that part has me confused :confused:

That being said, can we all agree that it is a better installation to run an ECG with the other conductors regardless. Treat the detached building panel as a sub panel, and seperate the neutrals and grounds?
 
Re: Sub Feed Ground

Originally posted by georgestolz:
So no neutral current will flow on the ground rod, since they are not connected together (in a direct sense).
EGC run with the feeder or not there will always be (or the potential to be) current flowing through the earth between the separate grounding electrode systems.
 
Re: Sub Feed Ground

Originally posted by iwire:
EGC run with the feeder or not there will always be (or the potential to be) current flowing through the earth between the separate grounding electrode systems.
How's that? There's nearly zero resistance between them, they're connected through the EGC of the feeder. :confused:
 
Re: Sub Feed Ground

There's nearly zero resistance between them, they're connected through the EGC of the feeder. [/QB][/QUOTE]
 
Re: Sub Feed Ground

What would the second path for neutral current be, if there were no other metallic paths?

I guess I was meaning if there was a ECG conductor ran with the feeders and bonded again at the subpanel. If there is no ECG ran, and no other metallic paths back to service what is the neutral current path back to the service,since tne neutral and ECG are bonded at the subpanel?
 
Re: Sub Feed Ground

Originally posted by iwire: (800.33)Have you seen an instance where that would apply?
Not once. :D :D

It just occurred to me. The detached building predicament is the yen to the yang of 250.52(A)(1).

Yen: We can't really rely on the metal water pipe to interconnect electrodes, because a plumber might come along and stop the continuity.

Yang: We shouldn't rely on a neutral to perform bonding after the service, because a plumber might come along and add a metallic water pipe with continuity to the service.

Can we win? :D
 