Re: Sub Feed Ground
Not so fast.
How is it different than the 8.9 gazillion services to buildings in the United States?
Think of it this way.
Often the grounded conductor is much larger than the required grounding conductor.
The larger conductor provides a lower impedance fault path.
Lets say a 100 feeder is running 1500' feet to a pump house with nothing around it.
Would the 8 AWG EGC be be better than a 3 AWG grounded conductor.
I have never personally used 250.32(B)(2) as I was trained to pull EGCs. That aside it is an option I might use in certain situations.
This is Bennie's domain.
Agreed. [/QB][/QUOTE]That being said, can we all agree that it is a better installation to run an ECG with the other conductors regardless. Treat the detached building panel as a sub panel, and separate the neutrals and grounds?
Not so fast.
How is it different than the 8.9 gazillion services to buildings in the United States?
Think of it this way.
Often the grounded conductor is much larger than the required grounding conductor.
The larger conductor provides a lower impedance fault path.
Lets say a 100 feeder is running 1500' feet to a pump house with nothing around it.
Would the 8 AWG EGC be be better than a 3 AWG grounded conductor.
I have never personally used 250.32(B)(2) as I was trained to pull EGCs. That aside it is an option I might use in certain situations.
This is Bennie's domain.