Re: Sub Feed Panel
You bet i do.Thats the first time i ever had it exsplained that way.OUCH
You bet i do.Thats the first time i ever had it exsplained that way.OUCH
We like to think so, but the only way that is true is if the house is fed with a metal water service that is also bonded at the neighbors.Originally posted by crossman:
The difference is that the service panel is presumably at the same potential as the earth and sorrounding conductive items because it is tied to all of the "available electrodes" (or is that "present electrodes") and all of the equipment grounds are still at ground potential.
In this case it could be 120 volts.Originally posted by crossman:
If I am correct, plug in some reasonable ohm values for each part of the circuit, then do the Ohm's Law calcs and see how much voltage the fortunate man is subjected too.
This situation actually has nothing to do with tripping breakers under fault current. There is no fault at the moment. What I am saying is that using the "grounded" conductor as an equipment grounding conductor on the load side of the service has the potential to make the panel cans and any other equipment grounds and the frames of equipment HOT. No breakers trip because there are no faults.Originally posted by reel-break:
Am i totally missing something? If you disconnect the ground from the neutral at the original panel if the neutral isn`t bonded to the cabinet how does the equipment grounding conductor trip the breaker in fault.