I had an inspector say 2/0 AL isn't rated for 100amp sub panel but article 310-16 states otherwise. Is there an article that specifies wire sizing for sub panels? Any help would be appreciated. Thank You.
Again you cannot use ser at 75C but rather at 60C. If the feeder is connected to a 100 amp breaker then I see no issue- you are correctI am using SER and the 75 degree column still states its good for 135 amps.
I had an inspector say 2/0 AL isn't rated for 100amp sub panel but article 310-16 states otherwise. Is there an article that specifies wire sizing for sub panels? Any help would be appreciated. Thank You.